I am trying to send a setpoint to a rexroth analog controller from a step7 analog output (4 - 20mA) 6ES7332-5HD01-0AB0. Range of the lift is 1600mm. So 4mA = 0mm and 20mA = 1600mm. I have configured the analog channels to 4-20mA and mapped to QW8-15 in HW configuration. When I connect the following inputs to FC106, I would expect the OUT value to be half of 27648. But it gives me 10628 irrespective to the IN value.
TRUE--- EN
800.0 --IN -------RET_VAL 16#0000
1600.0 -HI_LIM
0.0 ----LO_LIM ---OUT 10628
TRUE ---BIPOLAR
Could someone pl guide me in the right direction.
Thanks
TRUE--- EN
800.0 --IN -------RET_VAL 16#0000
1600.0 -HI_LIM
0.0 ----LO_LIM ---OUT 10628
TRUE ---BIPOLAR
Could someone pl guide me in the right direction.
Thanks