Member
First off I know this can get very involved so I will attempt to respond with whatever questions you guys have. I know this is a very loaded question, so thank you in advance for any responses.
Disclaimer: I would never assume someone is giving 100% accurate advice, I will double check the work I just need some initial guidance.
So I have been tasked with showing a machine is safe using IFA's SISTEMA software.
This machine has 3 Light Curtains. (simplifying by assuming all same part #)
Operator Load: SL-V60H
Conveyor 1: SL-V60H
Conveyor 2: SL-V60H
All safety Relays are : 2700569
https://www.phoenixcontact.com/onli...y=usen&tab=1#Relayoutputs:enablingcurrentpath
All CR's are
Operator Light Curtain
Output:
Conveyor 1 Light Curtain
Output:
Conveyor 2 Light Curtain
Output:
Used to de-energize Hydraulic motor
Main Safety Relay: (2700569)
Inputs:
Energizes Safety Valve to allow for cylinders to actuate
Hydraulic Pump Safety Dump Valve Relay: (2700569)
Inputs:
Verifies Spool has shifted in Safety Valve
Hydraulic Safety Valve Relay: (2700569)
Inputs:
Safety Power:
So I believe I would need a safety function for:
Because these are so daisy chained together I'm kind of at a loss of how to do this.
I believe the safety function for the hydraulic pump would be:
Disclaimer: I would never assume someone is giving 100% accurate advice, I will double check the work I just need some initial guidance.
So I have been tasked with showing a machine is safe using IFA's SISTEMA software.
This machine has 3 Light Curtains. (simplifying by assuming all same part #)
Operator Load: SL-V60H
Conveyor 1: SL-V60H
Conveyor 2: SL-V60H
All safety Relays are : 2700569
https://www.phoenixcontact.com/onli...y=usen&tab=1#Relayoutputs:enablingcurrentpath
All CR's are
700S-CFB relays.
Operator Light Curtain
Output:
OSSD1: OP CR1
OSSD2: OP CR2
OSSD2: OP CR2
Conveyor 1 Light Curtain
Output:
OSSD1: Conv1 CR1
OSSD2: Conv1 CR2
OSSD2: Conv1 CR2
Conveyor 2 Light Curtain
Output:
OSSD1: Conv2 CR1
OSSD2: Conv2 CR2
OSSD2: Conv2 CR2
Used to de-energize Hydraulic motor
Main Safety Relay: (2700569)
Inputs:
Power: Constant
CH1. N.C. E-Stop 1 & N.C. E-Stop 2
CH2. N.C. E-Stop 1 & N.C. E-Stop 2
Reset: N.O. Power On Push Button & N.C. MCR1 & N.C. MCR2
Output:CH1. N.C. E-Stop 1 & N.C. E-Stop 2
CH2. N.C. E-Stop 1 & N.C. E-Stop 2
Reset: N.O. Power On Push Button & N.C. MCR1 & N.C. MCR2
MCR1 A1
MCR2 A1
MCR2 A1
Energizes Safety Valve to allow for cylinders to actuate
Hydraulic Pump Safety Dump Valve Relay: (2700569)
Inputs:
Power : N.O. MCR1 & N.O. MCR2
CH1. N.O. OP CR1 & ( N.O. Conv1 CR1 or N.O. Conv2 CR1)
CH2. N.O. OP CR2 & ( N.O. Conv1 CR2 or N.O. Conv2 CR2)
Reset: Output of Hydraulic Safety Valve Relay
Output:CH1. N.O. OP CR1 & ( N.O. Conv1 CR1 or N.O. Conv2 CR1)
CH2. N.O. OP CR2 & ( N.O. Conv1 CR2 or N.O. Conv2 CR2)
Reset: Output of Hydraulic Safety Valve Relay
Safety Valve Sol 1
Safety Valve Sol 2
Safety Valve Sol 2
Verifies Spool has shifted in Safety Valve
Hydraulic Safety Valve Relay: (2700569)
Inputs:
Power : N.O. MCR1 & N.O. MCR2
CH1. N.C. switch 1 on Safety Valve
CH2. N.C. switch 2 on Safety Valve
Reset: Auto
Output:CH1. N.C. switch 1 on Safety Valve
CH2. N.C. switch 2 on Safety Valve
Reset: Auto
Goes to Reset of Hydraulic Pump Safety Dump Valve Relay
Safety Power:
N.O. OP CR1 & N.O. OP CR2 & (( N.O. Conv1 CR1 and N.O. Conv1 CR2 ) or ( N.O. Conv2 CR1 and N.O. Conv2 CR2 ))
So I believe I would need a safety function for:
Shutting off Hydraulic Pump
Shutting off Hydraulic Safety Valve
Conv 1 Stop condition
Conv 2 Stop condition
Shutting off Hydraulic Safety Valve
Conv 1 Stop condition
Conv 2 Stop condition
Because these are so daisy chained together I'm kind of at a loss of how to do this.
I believe the safety function for the hydraulic pump would be:
Inputs:
CH1. N.C. E-Stop 1 & N.C. E-Stop 2
CH1. N.C. E-Stop 1 & N.C. E-Stop 2
Controller:CH1. N.C. E-Stop 1 & N.C. E-Stop 2
2700569
Output:700S-CFB
Has dual channel, with edm monitoring which would make it class 3 or possibly 4, is that correct?