How to open a Plc5/80 program using Rslogix 5000

BTL_Man

Member
Join Date
Nov 2007
Location
N.C.
Posts
3
Is it possible to save or export an RSlogix5 Plc5/80 program in a way that it can be opened using RSLogix5000..?
 
Are you tring to open a PLC5 file for editing? If so, then you need RSLogix 5.


If you are looking to convert the code to ControlLogix, then you could "Translate" the PLC5 program to ControlLogix. Look under the Tools tab, then Translate PLC5/SLC.
 
It's pretty straightforward. In Logix5 save your file as a .PC5 file. Then do Tools-> Database-> ASCII Export and ensure that under the AB6200 tab you're exporting the Address/Symbol as a .txt file

In Logix5000 do Tools->Translate PLC/SLC and fill in the blanks. Don't expect to get 100% done for you, there'll almost certainly be a list of exceptions to go through. Then in Logix5000 do File-> Open but remember that you're looking for a .L5K file rather than .ACD. You'll be asked if you want to import, you won't get anywhere by saying no!


 
But even then it won't be a PLC 5/80 program anymore. It'll be a program for a ControlLogix. And the addresses will be all messed up. And some instructions won't convert nicely -- or won't look like they used to in the 5/80.
 

Similar Topics

Have a file that a technician had on a floppy disk in one of our plants. It is a machine that a outside integrater was used, and integrater now no...
Replies
3
Views
3,390
I am using Factory Talk view Machine Edition Runtime HMI. I want to configure on button in such way that when i press this button I want to...
Replies
3
Views
117
hello I have 7cp476 cpu why can led always open and No connection
Replies
1
Views
133
Anyone have issues with RSLinx being very slow to open. It sometimes will say "Checking Activation" at the bottom for what seems like an...
Replies
2
Views
154
Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
Replies
8
Views
337
Back
Top Bottom