InTouch, Unity, addresses dont match

Milestogo

Member
Join Date
Aug 2019
Location
Montreal
Posts
19
Hello,

I'm running my Plc in PLC Simulator (Unity Pro XL).

Intouch sees the connected links but the tags are not matching
(+1 on InTouch).. o_O

example :
Intouch : %MW1950 Equals %MW1950 on the PLC datas.

I've been told it has something to do with the NodType.
It was set to Modbus by default, since most of our other plcs on the network are configured that way. This one PLC is Tsx premium..

Is there a way to adjust the starting address, either on Unity or SMC perhaps?

Thank you for your hindsights!
 
Generaly Modbus drivers have in configuration option to select if addressing is normal or +1. As I record InTouch has it, but I didn't use it for quite awhile.
 
Hello,

I'm running my Plc in PLC Simulator (Unity Pro XL).

Intouch sees the connected links but the tags are not matching
(+1 on InTouch).. o_O

example :
Intouch : %MW1950 Equals %MW1950 on the PLC datas.

I've been told it has something to do with the NodType.
It was set to Modbus by default, since most of our other plcs on the network are configured that way. This one PLC is Tsx premium..

Is there a way to adjust the starting address, either on Unity or SMC perhaps?

Thank you for your hindsights!

This is normal, it's just that the PLC will be 0 based, the driver in InTouch 1 based so need to add an offset, in most SCADA applications you can change this with driver settings if required.
 

Similar Topics

Hello, AVEVA OI system drivers such as ABCIP and MBTCP provide a discrete register called $SYS$STATUS, which can be tied to a Discrete tag in...
Replies
0
Views
36
Hi all. Weird thing happening. I do a "set" from a button for a command (direct Discrete Value, no script), waiting for the L82 PLC to set it...
Replies
1
Views
64
I am currently working on converting an Object-based ArchestrA System Platform HMI to a Tag-based InTouch HMI. Currently, the I/O is linked...
Replies
0
Views
54
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
Replies
0
Views
107
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
7
Views
268
Back
Top Bottom