Is it possible to link an HMI across VMs
robertmee
Feb 2008
NC
2,049
In the past when testing a particular HMI with a CLX program I'd use rsemulate with rslinx virtual backplane driver and create a dde topic for the hmi pointing to the clx program in emulate. I have a project with wonderware on a virtual machine the customer provided me...I'd rather not have to rebuild linx, logix, emulate and all the aops on the wonderware vm. So is it possible to just install linx on the ww vm and have it somehow point to the emulator running on a different vm?
Do you have an RSLinx Classic Gateway license running on that Emulator VM ?
As tricky and frustrating as Remote OPC can be, that's the first thing I would try, to use the VM with Emulate 5000 and RSLinx Classic as a Remote OPC Server.
Another thing to try would be to put only RSLinx Classic on the Wonderware VM, and set up the Emulate 5000/RSLinx Classic VM as an RSLinx Gateway, which would let you use the "Remote Devices via Linx Gateway" driver on the Wonderware/RSLinx VM.
I have full license on both VMs....I saw the remote server via gateway driver on the WW VM but was unsure how to set it up as when browsing for a server nothing shows up. I'll play around with that idea and see how far I get.
This is something you would want to use SoftLogix instead of RSEmulate, however I know SoftLogix isn't much of an option after v20 and I'm not sure if AB is improving RSEmulate...
I've done many virtual setups where a VM is running a Softlogix and many other VMs are either IO servers, Runtime Clients, Development clients...etc. All virtualized. Largest setup I did was ~20 or so VMs total, included redundancy.
Softlogix makes it just like a physical PLC w/and IP address. Go that route if you have the option.
Hi all I have a project that uses a Siemens 315-2DP and two HMI's. The two HMI's are at separate ends of the line. One of the HMI's has a...
2,976
I have ML1500 and PV1000+. I would like to display the parameter value in the ML1500 on the PV1000+. The following configuration is impossible or...
3,946
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
256
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
399
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
213