Issue with '.PC' signal from MAH command on RSLogix5000 Ver20 & SERCOS Ultradrive

Eoghan

Member
Join Date
Oct 2013
Location
Galway
Posts
37
Morning.
Have a 2 Sercos Ultra 3000 drives configured onto RSL5k Version 20.
Drive are configured for active homing to switch and pulse.
Both drives are positioning correctly using MAM commands and giving me the '.pc' output from Function Block.

But I never get the '.pc' output after executing the MAH command. MAH command 'works'- in that it sends the axis to find the home switch and stop at this position once detected. I end up having to program a MAM command to position zero after the MAH command to ensure I know axis is physically at zero.

After MAH motion stops, the axis position display is non zero - varies between 0.5 and -0.5 mm. It is as if MAH command stops executing before it finds actual position.

Have tried upping Kp Gains and homing to switch but has not helped.

ANy suggestions as to what configuration might be inhibiting the MAH performance. Screenshots of motor config attached

MAH.jpg
 
Two questions:

Are you keeping the MAH instruction always active, or only on the rising edge?

Does the Axishomedstatus comes on when the servo stops (using the MAH instrucion?
 
Morning.
Have a 2 Sercos Ultra 3000 drives configured onto RSL5k Version 20.
Drive are configured for active homing to switch and pulse.
Both drives are positioning correctly using MAM commands and giving me the '.pc' output from Function Block.

But I never get the '.pc' output after executing the MAH command. MAH command 'works'- in that it sends the axis to find the home switch and stop at this position once detected. I end up having to program a MAM command to position zero after the MAH command to ensure I know axis is physically at zero.

After MAH motion stops, the axis position display is non zero - varies between 0.5 and -0.5 mm. It is as if MAH command stops executing before it finds actual position.

Have tried upping Kp Gains and homing to switch but has not helped.

ANy suggestions as to what configuration might be inhibiting the MAH performance. Screenshots of motor config attached
Issue resolved with the attached Rockwell Knowledgebase Entry 22214:
22214 - When executing a ControlLogix MAH instruction, (Motion Axis Home) the .PC bit (Process Complete) is never set


Access Level: TechConnect
Date Created: 06/28/2002 12:00 AM
Last Updated: 02/25/2013 09:16 PM

When executing a ControlLogix MAH instruction, (Motion Axis Home) the .PC bit (Process Complete) is never set.

Problem: On a Uni-directional home, the .IP bit is cleared, the AxisHomedStatus is set, but the .PC bit is not set.
Cause: If the home direction is uni-directional and the home offset is less then the distance required to decelerate, then axis is simply decelerated to a stop. The axis does not reverse direction to move to the home position. In this case, the .PC bit of the MAH instruction is not set. The .PC is set when the axis stops at the configured home position.
Verify:
Cure: To get the .PC to set, set the home offset to a value greater then the distance required for the axis to decelerate. To compensate for the home offset, set the home position to be the same as the home offset. For example. If the desired position at the marker is 0.0. When a uni-directional home is done, when the marker is seen the axis will move and decelerate to the position as defined by the home offset. This position is now defined as the Home Position. If the marker position should be 0.0, then make the home position equal to the home offset.
 

Similar Topics

Hello, I’m new to this forum and if I’m posting incorrectly let me know. I’ve been having an issue I can’t seem to figure out. I’m sure it’s...
Replies
1
Views
134
Hello all and thanks in advance for the help. I have been asked to use an existing drive with a new control system. At the moment I have it fully...
Replies
8
Views
7,416
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
Replies
3
Views
108
Hello all. I am trying to communicate to an ASi gateway from my CpLX (L16ER). I am able to ping the gateway and it replies. I configured the...
Replies
4
Views
119
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
16
Views
319
Back
Top Bottom