KepServerEnterprise V5 Factorytalk View ME and S7 300

Kolberg

Member
Join Date
Nov 2007
Location
Silkeborg
Posts
10
Hi all

Im trying to connect a PanelView Plus 600 with a Siemens S7 315 processor over ethernet. I have configured the KepserverEnterprise and i have downloaded a new firmware (with kepserver) into the panelview. The problem is, that my Factorytalk View application is working on my computer (altering values in the PLC), but when i download the application into the panelview - there is no connection at all. It seems that the Kepserver information (*.pfe) isn´t included in my *.mer file - what am i doing wrong??
 
Currenly, the KEPServerEnterprise V5 release only supports the Desktop. The CE release for KEPServerEnterprise is still the V4 release. Projects configured on the desktop in V5 will not load into the panel and run becuase the versions to do not match.
 
Thanks Fred. I have allready talked to Ab support about the problem, and they said the same. So no i have downgraded my KepServerEnterprise from a V5 to V4 according to a list i found i a AB technote. The problem is now, that my FactoryTalk View application doesn´t even work on my computer now - but i hope to get some results within the next hour or two.....
 
Hi Fred
After spending a unknown amount of time with V5 (without any succes), i switched to V4 - and now everything is working.
 

Similar Topics

I have Rockwell software as described below. FactoryTalk View Studio SE Version 8. RSLinx_Enterprise connecting all my ControLogix devices...
Replies
8
Views
2,439
i have already try the KepServerEnterprise from rockwell and its seems to work well with a few Tag im Wondering if there is limitation with...
Replies
3
Views
8,018
Hi team, I try to use global connections but don't know how to use them. Can anyone explain to me how to configure it
Replies
2
Views
12
As the title says, all of the client HMIs at the plant freeze up for about 5-10 minutes everytime I or a vendor make new routines or new tags in...
Replies
4
Views
62
Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
Replies
6
Views
118
Back
Top Bottom