I have recently received a piece of equipment from an oem with an Allen Bradley Pico controller. I have pulled wires and set it up to run using a 1756-OW16 output card to drive three inputs from a supervisory Controllogix processor. The problem is the outputs have a small leak current that activates the inputs on the Pico controller even when the outputs are off. My quick fix was to put a small light bulb as load to bleed off the stay current and pull the voltage to zero. This has worked up to now, but this is not the best solution. What I think I need is a high resistance load resistor to pull down the leak current. Does anyone know what value/wattage I should use for this?
 
OW16 is a relay output card so I don't see how you could be getting any leakage current. When the output is off, there is a mechanical break in the circuit. Is your control voltage 24VDC?

If I need to pull down an output or input, I typically use a 1/4W 10K resistor. The optoisolators on PLC inputs generally operate in the <10mA range, so this is more than sufficient.
 
Thanks for posting the details on relay contact outputs that leak current. That was news to me. Who'd a thought . . . .?
 
Thanks for posting the details on relay contact outputs that leak current. That was news to me. Who'd a thought . . . .?

That got me with a flex relay output module once. Spent a couple hours troubleshooting before I got the manual out.
It ran fine for a few years with nothing but solenoid loads. We then connected an electronic strobe light, it worked fine when the relay was pulled in
but when the relay was open the light would blink about every 8 min. Something in the light was apparently charging up thru the leakage. I thought how could this be, its a "relay".
 
Last edited:

Similar Topics

I cannot find anything anything in the manual for a load resistor, does this PLC not have any built in? Is it a dipswitch setting?
Replies
4
Views
1,925
When i load my client a[plication the following error is recorded in factorytalk view studio log Failed to load data server...
Replies
0
Views
48
Background for the question: A service man from a sub-supplier has made changes onsite to a Siemens PLC and HMI program. He has not made a backup...
Replies
7
Views
286
I have a 90/30 CPU331. I am trying to upload the program out of the CPU and keep getting an error uploading the logic. Error 8262: Error...
Replies
6
Views
120
I am connecting to a remote device. When attempting to upload I receive an error that states: Error: Auto_Functions: The Import was aborted due...
Replies
3
Views
198
Back
Top Bottom