Logix 5575 - Get Redundant Power Supply Status

Tanquen

Member
Join Date
Jul 2014
Location
CA
Posts
163
I’m using RSLinx to get some of the built in diagnostics items from the PLC. Like @ProcessorName, gets you the name of the program running in processor. Is there nothing for the connected redundant power supplies?
 
There is not.

ControlLogix power supplies do not communicate with the CPU over the backplane, nor does the CPU have the ability to read voltages or discrete signals across the backplane connector.

The Redundant power supplies like the 1756-PA75R have an onboard solid-state output contact for their status, which you would have to wire into a discrete input somewhere in the I/O system.
 
Thanks for the info. That is the way it was looking, I was just thinking that something may be coming through those crazy huge cables from each of the power supplies.
 

Similar Topics

Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
Replies
10
Views
399
ControlLogix 5575 (L75): Sudden/Repeating "Unconnected Message Timeout" (0204) This ControlLogix PLC (L75/5575) has been in operation for at...
Replies
24
Views
10,829
So we have a few associates that like to write the date in the file name when saving the program to back it up. We back up the programs every...
Replies
12
Views
131
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
Replies
1
Views
52
Hello, I have a panelview plus that reads from 4 different PLC's. 2 of these used to be Micrologix PLC's and someone else went and updated them to...
Replies
3
Views
123
Back
Top Bottom