Manipulate Siemens SFB4-TON timer
Jobbe
Jul 2005
Antwerp
159
Is it possible to manipulate the standard SFB4-TON timer from Siemens in a VAT table? I need to do some qualification tests on a system with a few large IEC timers. With the default timers it is possible to overwrite the actual time with another value but it seems that this is not possible with the SFB 4 timers. The preset time is 72 hours and I would like to test the program by changing the expired time close to the preset time so I only have to wait a few seconds.
Temporary software changes to test the result of the timers are not acceptable, I may only change values through the VAT table. The preset time is also written in the software with an constant value, so I can’t change that either.
Subtract time from STIME in the instance DB to make the timer expire quickly. E.g. if your plc has only been running for a short time, enter t#-71h50m in STIME to make the elapsed time 71h50m + what ever time has so far elapsed.
Thanks!!
If I enter the value STIME = ATIME – wanted ET, I can manipulate it the way I want.
I was playing with the ATIME and STIME before but I could not figure out how to change them (never thought about entering a negative value).
Wow - I will have to test this!
For some time I have complained about the Siemens timers not paying attention to a change in the preset once they start timing. AB and GE timers don't do this. For example if a timer preset is 5 minutes and the timer is timing, I can change the preset to a value lower than the elapsed time and an AB or GE timer will be DONE. Not so with a Siemens timer. This does present usability problems in the field. Thanks for the thread, I will play with this "in my spare time".
Better to increment an integer on a timed interval. Compare against a preset.
I have an application with CIP motion drives Kinetix 5700 where I need to set the exceptions for "excessive position error" and "excessive...
1,053
Hi, I'm writing a program in Structured Text, and I'd like to create an array of INTs. However, I will sometimes need to operate on individual...
3,982
Is it possible to manipulate an object's properties from the PLC? FactoryTalk ME perhaps vary the length of a line or height of a panel or...
1,339
Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
43
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
205