Hello Siemens experts.
Trying to figure out how to change the I&M data of a Profinet device with TIA Portal, and I can appreciate advice from the experts as so many times in the past. I have tried to change the I&M data in the TIA portal project, then building the program with no errors. But, when trying to download the modified program, which must be different because the I&M data has changed, the TIA portal says:
"The configuration will not be loaded, because the online status is up-to-date. The configuration will not be loaded to module <<PLC NAME>>, because the online status is up-to-date."
As a result the I&M data in the device does not change.
It seems the TIA does not regard the change to the I&M data as a change to the PLC program. If I try using the online diagnosis for this Profinet device, I can see the actual I&M info but cannot change it. Is it possible that TIA portal does not allow the modification of I&M data, or more likely, my TIA Portal skills are insufficient?
By the way I am able to change the I&M data using PRONETA software and the licensed version of Profinet Commander, but I need to know if it is possible to change the I&M with TIA Portal.
Thanks very much for your words of advice.
Trying to figure out how to change the I&M data of a Profinet device with TIA Portal, and I can appreciate advice from the experts as so many times in the past. I have tried to change the I&M data in the TIA portal project, then building the program with no errors. But, when trying to download the modified program, which must be different because the I&M data has changed, the TIA portal says:
"The configuration will not be loaded, because the online status is up-to-date. The configuration will not be loaded to module <<PLC NAME>>, because the online status is up-to-date."
As a result the I&M data in the device does not change.
It seems the TIA does not regard the change to the I&M data as a change to the PLC program. If I try using the online diagnosis for this Profinet device, I can see the actual I&M info but cannot change it. Is it possible that TIA portal does not allow the modification of I&M data, or more likely, my TIA Portal skills are insufficient?
By the way I am able to change the I&M data using PRONETA software and the licensed version of Profinet Commander, but I need to know if it is possible to change the I&M with TIA Portal.
Thanks very much for your words of advice.