I have this module being used with a Controllogix 1756-M13/A. Using RSLogix5000 Version 8
I have an Exclamation mark on the I/O Configuration file and also on this module.
Looking in the Property box for this module I have the following
There are (2) Axis Listed (but not Lighted)
Revision 3.13 Electronic Keying: Compatibile Module
Connection Tab
Inhibit Module and the Major Fault boxes are not check
Module Fault
(Code 16#0203) Connection timed out.
Status: Faulted
Module Info Tab
Product Code: 1756-M02AE
Revision: 13.2
Serial Number: 000DB514
Status
Major Fault: None
Minor Fault: None
Internal State: (16#0034) Unknown
Configured: Yes
Owned: NO
Module Identity: Mismatch
I have never used this module but was setting it up to get some experience with.
Is this Mismatch issue I have due to the differences in the Version number or due to the Electronic Keying or both?
If it is the Electronic Keying just where do you find the correct numbers or such to change it?
As for the Version Differences I would have to upgrade the module from the 3.8 to the 13 correct?
If that is the case than I would also have to upgrade the Controllogix 1756-M13/A Processor too Correct?
Thanks All
I have an Exclamation mark on the I/O Configuration file and also on this module.
Looking in the Property box for this module I have the following
There are (2) Axis Listed (but not Lighted)
Revision 3.13 Electronic Keying: Compatibile Module
Connection Tab
Inhibit Module and the Major Fault boxes are not check
Module Fault
(Code 16#0203) Connection timed out.
Status: Faulted
Module Info Tab
Product Code: 1756-M02AE
Revision: 13.2
Serial Number: 000DB514
Status
Major Fault: None
Minor Fault: None
Internal State: (16#0034) Unknown
Configured: Yes
Owned: NO
Module Identity: Mismatch
I have never used this module but was setting it up to get some experience with.
Is this Mismatch issue I have due to the differences in the Version number or due to the Electronic Keying or both?
If it is the Electronic Keying just where do you find the correct numbers or such to change it?
As for the Version Differences I would have to upgrade the module from the 3.8 to the 13 correct?
If that is the case than I would also have to upgrade the Controllogix 1756-M13/A Processor too Correct?
Thanks All