MSG problems on slc network
lalion
Jul 2003
Ballarat, VIC, AUST
36
Hi, ive been having problems with existing messaging system on a dh-485 network with 4 SLC5/03 plc's.
The system has been in place running happily for years but this morning we found that 2 of the plc's would no longer talk via their rj45 port, I ended up replacing with 2 spare cpu's.
Now I can communicate with all plc's over network again with rslinx, but I have found that 2 MSG instructions on 1 of the plcs (one i didnt have to replace) is now no longer working, with error code 37 "Message timed out in local processor" on read msg instruction, and error 7 "Target Node does not respond" on write MSG, find screenshots attached.
Also I have noticed that neither EN or DN bits are energizing on the MSG rung when im online, even when using a manual toggle bit to trigger msg instruction, but S:2/7 "outgoing msg pending" bit is staying high on the SVC instruction rung.
Does anyone have any ideas of what might be happening or can give advice on things to try?
Thanks, leon
It's probably worth it to examine how the logic that triggers the MSG instructions is written. Although all the logic on those rungs is hidden in the screenshots, the presence of OTU instructions on the Timeout (bit 08) bits makes me think this logic might have been written as a combination of the SLC-5/02 style manual timeout and the simple self-retriggering examples found in the instruction set reference.
I suspect that the messages are all written to re-trigger themselves immediately on completion. This works great until one message fails, just like you can tailgate in traffic until somebody hits the brakes.
If you're happy with the power cycle results, go ahead and leave it as-is, but if you're interested in preventing such a logical buffer overflow in the future, post the logic, preferably in *.RSS format.
Thanks, leon
I ran into this problem a couple years ago. Ultimately, I resolved the problem by switching to SLC5/05 processors, but I did solve the problem on the 5/03 DH-485 network by changing power supplies until the problem went away.
Has the MSG routing always worked well? Can you post the logic you use to trigger the instructions?
Hi, I have a problem with a cpu slc 5/05 (1747-L552), 32k Mem 0S501 series C, I am using the MSG instruction to ethernet communication, it works...
9,332
We have a slc 505. It has about 12 msg instructions. The fiber on our DF1 ring got cut by a contractor. Got the fiber backup and 6 of the msg are...
22
4,951
This probably is something that I'm just overlooking but, I am having problems communicating two ControlLogix processors using the MSG instruction...
5,120
139
I have an 1769-L16ER that I use to test code and I just found that I can't create MSG tags at the local program scope - they have to be done at...
215