Multiple 2-Wire transmitter inputs, which power supply to use for loop power?

jfast

Member
Join Date
Apr 2012
Location
New Jersey
Posts
1
Hello,
I've a question regarding wiring analog inputs (4-20mA) to a compact-logix 1769-IF8 module.

The PLC and module exist already and are wired for 2-wire transmitter analog input, with loop power being derived from a 24VDC power supply in this panel. All 8 Analog input common terminals are jumpered together and bonded to DC- on this power supply (ANLG Com = V/l in 0- = ... = V/l in 7-) to avoid noise.

As a retrofit, I need to wire in two 4-20mA outputs from a device in the field, to spare channels on this slot. The outputs are coming from a Trane Programmable air handler control panel, model MP580. See pg 11 of manual:
http://www.wmitechnologies.com/pdfs/MP581-INFO.pdf

The MP580 has two universal analog outputs configured as 4-20mA. I am assuming they are not loop powered analog outputs.

Can I safely wire this analog output to my IF8 analog input, using my local 24VDC power supply to provide loop power? Or, do I need a loop isolator?

Thanks in advance! ... This stuff throws me through a loop for some reason.
 
Your field device must have an analog output to connect to your PLC's analog input.

I'll show you mine if you'll show me yours.

Here's a screen shot from the manual at the link you provide.

The terminal strip labeled analog outputs connects to a load labeled 0-10Vdc, not 4-20mA:

2dkpxd.jpg


The bottom sensor labeled 4-20mA sensor connects to an analog INPUT and is clearly connected to power supply, as one would expect for a loop powered sensor.

So unless you can show me where the 4-20mA output is, I'd say go buy a 0-10Vdc to 4-20mA signal conditioner.

For some small premium, you can get an isolated converter, to minimize the very high probability of a ground loop between the field instrument ground and the PLC analog input ground.

I would STRONGLY recommend an isolated converter.

There are loop powered converters, whose output is loop powered, like your other 4-20's on the AI.
 
Last edited:
So unless you can show me where the 4-20mA output is, I'd say go buy a 0-10Vdc to 4-20mA signal conditioner.

From page 4 of the same manual,see picture below.

But it appears to be an active output, so an isolator is still strongly recommended. As mentioned above by danw.

0-20ma to 4-20ma signal conditioner.

outputs.png
 
Last edited:
I concede, Mickey. You're incredible, reading through all the documentation!

Duh, I missed the significance of the "Load > 500 ohms".

They're driving the 0-20mA through a 500 ohm load to get the 0-10Vdc.

It bothered me that they mentioned 500 ohms, because I was thinking, "when was there ever a voltage AI with an input impedance as low as 500 ohms? Nowadays a voltage AI is typically 1Meg ohm." 500 ohms?

Too late after a long day at the grindstone.

Yes, still should probably have an isolator.
 
Last edited:

Similar Topics

This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
146
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
496
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
Replies
8
Views
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
Replies
1
Views
127
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
Replies
2
Views
170
Back
Top Bottom