Noobie question
black bear
Dec 2013
Bentham
Hi, I have been given task to solve operation of a machine controlled by an Allen Bradley SLC 5/01. Machine has been operated " out of sequence" which has resulted in several OTL being latched without any way of being unlatched stopping machine from running. Is it possible to unlatch all the OTL's (as initial startup) without communicating with the PLC?
I presume that if this is not possible, I would need: laptop running Rslinx, Rs500 Logix, 1747-UIC and 1747-C13 cable.
Going online with plc, I assume that the latched outputs can be forced to unlatch?
Dave
HMI? Is this human interface? No. Machine control panel has various operation switches and indicator lights. Two indicators denote latched parts of program which need to unlatch but this can only be done by illogic timers, counters and other latched OTL's. I only have printed ladder logic which was done in 1996 no changes to ladder logic have ever been done. There are some bugs in ladder but can be overridden manually. It is complex ladder of 300 rungs.
You are correct: you will need RSLogix 500 development/editing software, the RSLinx Classic Lite communication driver software, and the related 1747-UIC and cable.
Once you're online, you'll be able to highlight the incorrectly-latched memory bits, right-click, and select "Toggle". Or you can open the data table view and put a zero in the desired address.
Yes. You'll need to do as Ken Roach advises to be able to go online with the processor. Then, add some logic which can set the latches at startup (by this I mean powerup) - or at another time by designating a switch/bit for the purpose.
Thanks for replies, ordering hardware tomorrow, ~ £300. Hope comm's goes ok, I've heard that it can be tricky, i.e. Setting up correct drivers.
We have a 525 vfd that works without a PLC and just with field inputs. The speed reference is set with the help of embedded pot. Is it possible to...
1,497
Hello everyone I am new to Siemens Step 7 and having some issues I was going to add the a FC to OB1 (Network 28 In Image 1) But it was asking...
2,423
Greetings, I own and operate a small textile mill and suffer from the constant desire to improve things. The machines we use are made partially...
1,725
hello all brand new to this forum and also new to PLC programming. here's my dilemma, I am installing a PLC and a VFD Drive unit into a conveyor...
114
21,161
Scope: 1:Modify logic to allow automation of 4 new grain bins to existing grain leg system automated by 1769-l32e/a compactlogix controller v16...
2,405