Opc server is unable to load project controller CCW

FEGF

Member
Join Date
Mar 2023
Location
Carrollton
Posts
13
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
 
Upload means you want to transfer the program from the PLC to Laptop. Is this what you are trying to do?

OR

Do you want to download a program from your laptop to the Plc?

Once I know what you are trying to get done, I may have some answers for you.

But my first take on your problem is the Micro(820) program was wrote with a newer version of CCW.

If I was you the first thing I would do is to update CCW to the latest version.
 
No I am trying to get the program from the PLC to my laptop. I have CCW version 13 and the controller version 12.
 
Here's what I see. If the program in the PLC was created by a newer version of CCW it will not let you. Example: if program in PLC was created by version 20 then your version 13 will not be able to upload the program.

However if you get the latest version of CCW version 22 it will upload any version and convert.
 

Similar Topics

I have been using dotnet and OPC servers (NI and Kepware) to communicate with Allen Bradley Micrologix 1400 PLC on different environmental...
Replies
2
Views
5,801
If anyone has a crack for IBH OPC Server, please send it to: [email protected] Urgently. Thanks in advance!
Replies
1
Views
133
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
185
Hello everyone, I wanted to share my findings with getting the new OPC UA server working (I think you might be interested in this JeremyM :lolis:)...
Replies
8
Views
2,062
I have a Win10 64 bit host for my OPC DA server, which is Indusoft (Studio,Scada.OPC.3). Locally OPC works, Matrikon OPC Explorer. On my Win7...
Replies
5
Views
1,182
Back
Top Bottom