LJBMatt Member L Join Date Apr 2004 Location Dayton, OH Posts 430 Feb 4, 2009 #1 A question for those in the forum. Does anyone know if you are allowed to use Power Limited Tray Cable (PLTC) rated devicenet trunk in overhead drop ceilings without the use of a tray?
A question for those in the forum. Does anyone know if you are allowed to use Power Limited Tray Cable (PLTC) rated devicenet trunk in overhead drop ceilings without the use of a tray?
Derek Member D Join Date Dec 2008 Location Vancouver, WA. Posts 64 Feb 4, 2009 #2 PLTC-ER should be OK as it is rated for surface mount. It must also be plenum rated.
LJBMatt Member OP L Join Date Apr 2004 Location Dayton, OH Posts 430 Feb 4, 2009 #3 Derek said: PLTC-ER should be OK as it is rated for surface mount. It must also be plenum rated. Click to expand... That is what I was afraid of. I've been having no luck finding any truck cable that is plenum rated. Do you or anyone have a source?
Derek said: PLTC-ER should be OK as it is rated for surface mount. It must also be plenum rated. Click to expand... That is what I was afraid of. I've been having no luck finding any truck cable that is plenum rated. Do you or anyone have a source?
Derek Member D Join Date Dec 2008 Location Vancouver, WA. Posts 64 Feb 4, 2009 #4 I would call Belden and see if they have something that is rated for both tray and plenum.