OT: Panel Isolators
the_msp
May 2008
Northern Ireland
1,271
I normally go for the side of enclosure-mounted isolators. Sure, this means you can open the panel while it's live, however, to do so requires a panel key which your operator should not possess or have access to.
I have been asked for some upcoming panels for front door isolators, interlocked to the contacts on the chassis plate so it can't be opened live. Unless you push the little pin with a pen of course.
My experience with door isolators that are interlocked has generally been poor (17 years in Industry). E.g. they have no unlock pin, so they just get ham-fisted and twisted. Or the bar linking to the contact block drops out as you open the door. This leads to an isolator with no bar, and if say you had an emergency (e.g. fire, not E-stop scenario), you go to isolate the panel and you are turning thin air.
What is your experience and have you any recommendations for a brand that is easy to fit, can be unlocked with a pin to open when the panel is live, and seems to last the test of time?
3 phase 415V <100A
Avoid IEC style components, they are usually cheaper, made of more plastic than the NEMA counterparts, and have a history (for me) of failing exactly as you describe. I have in the past installed a proper disconnecting switch (Siemens, Square D, Eaton, etc) on the exterior of the cabinet (usually on the side wall, which doesn't directly address your problem) and then run the load conductors through a chase nipple or similar to the main contact block. This would also satisfy the "no energized conductors in the cabinet" problem that seems to be more prevalent these days.
The best way i have seen to do this is have a key switch on the front to bypass the circuit if you need to open energized. This relies on the key being available when need , we leave our keys in the panel door.
I've taken to using the ABB OT40F3 isolators. You can buy them as a unit or as separate switch, rod and handle. They're not expensive, they're reasonably solid and they don't droop if they're mounted right.
I use front mounted ones and they have the little pinhole to open because...
The operators will go out and buy their own panel key.
It is a problem that has never been properly assessed by any ruling body.
Even using an interlocked front isolator restricting entrance until the power is turned off still leaves live conductors in the panel.
Isolator should mean just that - it is totally isolated.
A side isolator where the mains is connected and a key system for the door should suffice for the regulations and your culpability.
If an operator or whoever does not turn the isolator off and gets the door open then the onus is on him/her not the panel maker.
I'm only throwing this out there for discussion but I have come across a few of these the last few months and I wondered if the regs had changed...
1,877
We have boiler control system runs on A-B PLC. The interface is A-B Panel View Plus 7, mounted on the local control panel very near the boiler...
44
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
45
I HAVE B&R POWEL PANEL 400 HMI. THE ISSUE IS HMI NOT BOOTING, DISPLY SHOWING CONTIUESLY (ATTEMPTING TO A BOOT HARD DRIVE....)
74
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
115