That PanelView part number ending in (9) means that it has a DH-485 protocol network port with RS-232 signal and connector type.
That means you can connect it only to devices that run DH485 protocol over RS-232. That includes a 1761-UIC PC interface, or a MicroLogix controller with its serial port set for DH485 network mode.
The
PanelView Standard User Manual shows that the recommended part numbers for a direct connection to a MicroLogix with a Channel 0 round "Mini-DIN" port is 2711-NC21 or 2711-NC22.
Many users also use a 1761-CBL-PM02 and add a null-modem converter to the DB9 end.
Because the MicroLogix 1200 has a +12V pin on the Channel 0 serial port, you should use only A-B cables. If you build your own, look up the pinout.
To my knowledge, the MicroLogix 1200 with the "R" part number supports only DF1 Full Duplex from the second serial port, so you will have another method for connecting to the PLC even when Channel 0 is set for DH485 protocol, without even having to use the DCOMM button.