I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.
 
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.

What is that input coming from? Can the device you're monitoring create an inductive spike when it turns off? Can you use an interposing relay on that input?

A properly rated MOV in parallel with the input, and connected to ground may help.

-rpoet
 
Since we're talking about it, can anyone recommend a MOV or snubber they'd recommend to put across the coils?

I tried picking one out on Mouser a few weeks ago, but all the choices are overwhelming.
 

Similar Topics

Hello, I am a plc engineer and I have a job to do in the NIGERIA 25000 TON GRAIN SILOS STORAGE CONTROL PANEL. A problem where the panel is not...
Replies
1
Views
108
GitHub Link: Open Industry Project This is a side project I've been working on for some time. The goal is to provide an open platform for...
Replies
0
Views
121
Dear All, Currently i'm working with Endress Hauser flowmeter and AB PLC and try to integrate with 2 items. Flow meter spec using is Promass...
Replies
6
Views
154
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
Replies
2
Views
63
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
5
Views
148
Back
Top Bottom