PowerFlex 525 Fault Input Anomaly

Join Date
Nov 2021
Location
United States
Posts
42
All,

I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I was able to achieve the power restart by using a First Scan latch that cycles the Start command until the drives are at reference. This worked perfectly and have no complaints with the logic.

The issue arises on the Fault side. I added the Input an XIO PF_525:I.Faulted to an Interlock rung in series with all instructions on the Start command rung. This single bit seems to be dropping out the signal and bringing it back up on Power Up anyways.

Can anyone confirm that this is a known function of the input from the drive?

Edit: I have AFI'ed the S:FS bit preventing the bit to latch on first scan, and it still auto restarts on power up.
Taking the PF_525:I.Faulted bit out of the interlock does prevent the machine from starting unless the First Scan logic is running.
I have also checked the drive for parameters A541 and A543; both parameters are not enabled.
 
I don't think anyone here will recommend starting an agitator motor up after power cycle or fault with out some user input like a reset/start pushbutton.

I suggest using an audible alarm do to notify about a power cycle or fault and have the operator start things how they typically would to ensure safety.
 
I don't think anyone here will recommend starting an agitator motor up after power cycle or fault with out some user input like a reset/start pushbutton.

I suggest using an audible alarm do to notify about a power cycle or fault and have the operator start things how they typically would to ensure safety.
Thank you, but I was more so wondering if anyone knew why the Faulted XIO from the drive was cycling the input after a power loss.
 

Similar Topics

So our Powerflex 525's are set up to allow REMOTE operation from PLC through network. But if network is lost we want to be able to run in LOCAL...
Replies
5
Views
614
I recognize that I need to factory reset the drive and that P053 is my ticket. Problem statement: I can't get passed the fault display to get to...
Replies
5
Views
1,708
I am getting a motor stalled fault on a VFD for a incline conveyor motor with a electric brake. I notice that when the VFD is supposed to ramp...
Replies
5
Views
4,361
We have a powerflex 525 VFD and today got a F012 Fault on it which is HW over current. I am not really sure what a Hardware Overcurrent fault is...
Replies
3
Views
3,192
Good Morning , I have some new Powerflex 525 Drives - This morning I got a F 114 uC Fault. Sounds like it is an issue with the microprocessor...
Replies
11
Views
14,122
Back
Top Bottom