drinck7
Member
Hello,
I have a PowerFlex 753, firmware 14.004. I am trying to turn on ADC, but when I do, the VFD will not reconnect to the PLC. When I open the AOP, the drive looks like it starts uploading, then says ADC configuring, and just loops between these two. The only way for me to get the drive to reconnect is to go offline, turn off ADC and re-download to the controller. My AOP is version 5.07.91.0
The Steps for turning on ADC I am using:
1)Upload params from drive
2)Save/Upload tag value from controller
3)Flash NVM on controller
4)Go offline, enable ADC and Download to PLC.
I have 3 other 753s (1 of which is 14.004, and 2 that are 14.002) and ADC is enabled and working on those.
Any help would be appreciated. Thank you in advanced!
I have a PowerFlex 753, firmware 14.004. I am trying to turn on ADC, but when I do, the VFD will not reconnect to the PLC. When I open the AOP, the drive looks like it starts uploading, then says ADC configuring, and just loops between these two. The only way for me to get the drive to reconnect is to go offline, turn off ADC and re-download to the controller. My AOP is version 5.07.91.0
The Steps for turning on ADC I am using:
1)Upload params from drive
2)Save/Upload tag value from controller
3)Flash NVM on controller
4)Go offline, enable ADC and Download to PLC.
I have 3 other 753s (1 of which is 14.004, and 2 that are 14.002) and ADC is enabled and working on those.
Any help would be appreciated. Thank you in advanced!