Problem v17 to 24 logix5000 conversion

Join Date
Jun 2017
Location
Manila
Posts
3
Good Day Sirs!

I'm now having problem on a system that runs formerly in version 17. I upgraded it to version 24. I simply Upload the program then change the version and then downloaded it to the new v24 processor. I'm Having issue in the analog input modules because of its wrong reading, it has now an offset during its Low Signal. What am I missing here? Thank You for those who will response.

Ralph
 
Hi max.

The module settings of high and low engineering is defined in the configuration tab in the module. No other logic control these parameters.

I think i see the problem. There is a minor fault. Chxx.calfault is set to 1. Is it normal when you change to a new cpu, the calibration settings should be calibrated again?

Thankyou for your reply guys.
 

Similar Topics

I was working on a new system upgrade where we were replacing a TI PLC with AB PLC. Other parts of the system had AB PLC (ControlLogix L61) with...
Replies
4
Views
3,885
Hi everybody, We have a Powerflex700S Phase2 Drive in use. To set this Drive up I used the Startup Wizzard from Drive Executive (Autotune etc.)...
Replies
2
Views
2,630
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
Replies
0
Views
53
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
Replies
0
Views
75
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
78
Back
Top Bottom