PV550 Upload Issue

PLC Pie Guy

Member
Join Date
Jun 2013
Location
Halifax
Posts
1,144
Good Morning Folks.

Win Xp, PRO, Version 2002, SP3
RSLinx Classic 2.54
Using the AB UIC-485 driver with the 1747-UIC and a 2711-NC13 connected to an old PV550, 2711-K5A5 on Node 2.

Linx sees the PV550 just fine.

Going into the upload configuration screen I have selected the transfer type as DF1-Point to Point -- RSLinxAB_UIC-1.

Every attempt to upload says error : "2258 - Unable to communicate with operator terminal, did not receive a response"

"Verify Cable Connections"
"If you are using a DF1 Point to Point, insure that the PanelView does not have its printer port enabled"


Anybody have any tips?

Thank you.
 
Error2258 upon upload after successful comms with Linx = Try to upload with Transfer type set to "RSLINX Network"

Works perfectly!

Thanks
 

Similar Topics

I have PV550 2711-A5B5, I want download program to PV. I have USB to RS232 adapter. and a laptop. How can I do to download my program? The...
Replies
16
Views
8,327
One of our customers has an issue with the display on their PV550. This is not a system we installed so we don't have the original program. They...
Replies
6
Views
5,867
I'm trying to download an aplication to a PV550 RIO, with keypad & touch screen, but it's too long. I know that I can do it without the upload...
Replies
3
Views
3,846
Greetings!Anybody could help me regarding my problem with my machine?The problem is this,i want a back-up program of this machine because i have...
Replies
1
Views
3,321
Hi, I just uploaded a Panelview 550, there is some error along the way - tag missing -. When I check the tag, I can find the tag name but not the...
Replies
2
Views
5,242
Back
Top Bottom