Q71E71-100 ERROR CODE C017

PLCINPROGRESS

Member
Join Date
Feb 2024
Location
Kentucky
Posts
1
Error description: "A connection could not be established in the open process of the TCP connection."
Action:
•Check the operation of the connected device.
• Check the open process of the connected device.
• Correct the open setting of the communication parameters.
• Correct the port number of the Ethernet module, the IP address and port number of the connected device, and the open setting.
• Check if the cable is disconnected.
• Check if there is a problem with the connection to the transceiver or terminating resistor.

Does anyone know how to clear this error code? I have followed the recommended step (found above) and connection tested and everything is working fine however this error is still remaining.
 
When you say "clear" the error, do you mean the "com.err" LED? or clear the fault itself.

If you go into ethernet diagnostics, you can press the "clear err LED" button, if the fault still exists, the LED will eventually come back on.
 

Similar Topics

I am installing a kinetix 5100 on a machine, driving a MPL servo, and it's my first time tuning a servo PID. I'm happy enough with the behavior of...
Replies
10
Views
265
Hi guys, I have the first Kinetix 5100 in my facilities. I already configure the movement in Speed Mode, I am sending the Analog signal from my...
Replies
1
Views
75
Hello all I was trying to autotune a Kinetix 5100, I got an encoder fault and it says to check the wiring. I remove the 24 volts from drive to...
Replies
0
Views
76
I am using Schneider elau pack drive servo motor ISH-100. I am facing the problem that On the ISH -100 red light is blinking and pack drive C-600...
Replies
0
Views
92
Back
Top Bottom