Hi everybody,
I have a doubt o_O. I will program a PLC but I'm not secure if the values the word "N7:0" be deleted in case of a power failure or shut down. I need to keep these data!. how make this?
Thanks in advance
PD: I'm programming in Rslogix500 :)
if the data does not change than simply program a 1st scan pulse to load the data into N7:0
Otherwise
the data table will remain in the event of a power failure.
You do need to alert people if the batery is low.
As long as the Battery is in good condition, Data in the N7 File will be retained through a power failure. I have seen the Data retained in a SLC500 for several months without power.
Stu....
Most data table values in SLC and MicroLogix controllers are "rententive" during a power cycle. The controller battery keeps the RAM memory running during power cycles for many months.
The Input data table and the Status data table (I1 and S2) are managed by the controller operating system so they are not considered "rententive".
Any data table element that is written to by ladder logic will have its value determined by the user program.
But all other values are rententive.
There are some subtleties to this issue, including the use of nonvolatile memory devices (EEPROMs) and the way in which some HMI devices implement powerup values.
But in general if you write a value into N7:0, then turn the controller off and walk away, when you turn the controller back on the same value will still be in N7:0.
Hello! I have a datablock in a PLC witch contains about 700 variables. I must save this data once a day on a Windows PC in a XML or CSV file. Eg...
503
Using Allen Bradley PLCs, What are some easy ways to save process data from the PLC to a computer ? Would I have to start getting into SQL type...
18
10,819
Hello friends I have a PLC5/20, I need to save 2 tags to a excel datasheet. This tags are: barcode, press force. I need to save the barcode and...
3,544
Hi all, I am reading temperature from the analog modules, for the first stage of the experiment, I will keep my micrologix 1200 connected with the...
5,268
I'm a bit stuck again... See the redacted picture. At the moment, pressing F7 saves the "live" laser measurement into the boxes indicated by the...
1,121