I have a customer who wants me to make a control panel for a single motor (480VAC) but they are supplying the start/stop signal from a remote drive. They want a push-button station with a safety disconnect (within sight of motor) and will send a separate 120V source for the controls.
My question is for best practice on the 120VAC. I obviously will fuse the hot side – but should the neutral be fused? Should I have some kind of load switch or disconnect on the inside of the panel for the 120VAC? It seems goofy to me to have two disconnect switches on the outside of the panel – but maybe that is the way to go?
I’m also assuming I should ground/bond both the 480VAC and the 120V neutral like usual – even though I’m getting them from two different sources?
Thanks for any/all input.
EDIT:
So I was just looking and I think what I plan to do is use a rotary disconnect with two AUX contacts to run the 120VAC source through. This way a single disconnect will remove both sources for opening the panel.
My question is for best practice on the 120VAC. I obviously will fuse the hot side – but should the neutral be fused? Should I have some kind of load switch or disconnect on the inside of the panel for the 120VAC? It seems goofy to me to have two disconnect switches on the outside of the panel – but maybe that is the way to go?
I’m also assuming I should ground/bond both the 480VAC and the 120V neutral like usual – even though I’m getting them from two different sources?
Thanks for any/all input.
EDIT:
So I was just looking and I think what I plan to do is use a rotary disconnect with two AUX contacts to run the 120VAC source through. This way a single disconnect will remove both sources for opening the panel.