Siemens 60W 120/230V power supply on 100V rated voltage

doomsword

Member
Join Date
Aug 2016
Location
Zagreb
Posts
201
Very simple question, can Power supply module PS 60W120/230V AC/DC(6ES7507-0RA00-0AB0) work on 100 V AC voltage?

Basically can this power supply work in Japan?
 
Supply voltage
Type of supply voltage AC/DC
• Rated value (DC) 120 V / 230 V
• Valid range low limit (DC) 88 V
• Valid range high limit (DC) 300 V
• Rated value (AC) 120 V / 230 V
• Valid range low limit (AC) 85 V
• Valid range high limit (AC) 264 V
• Short-circuit protection Yes
Mains frequency
• Rated value 50 Hz Yes
• Valid range, low limit 47 Hz
• Valid range, high limit 63 Hz
Power failure backup
• Power failure backup time 20 ms

Lowest it will work on is 85V AC or 88V DC so I'd say you're good to go.
 

Similar Topics

I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
6
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
8
Views
96
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
2
Views
89
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
Replies
0
Views
65
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
4
Views
121
Back
Top Bottom