Siemens 6ES7 331 7FK02 0AB0
hutch1980
Jun 2020
california
I've been fighting a problem with this 8 channel analog input card mentioned in the title. I believe it's something I'm doing in the wiring but can't seem to figure it out. On one remote rack I have two analog inputs from two separate drives going into one of these boards and neither one is reading from the plc. The drive display shows 4mA output and I read 4mA with my meter but from the logic side it shows 32767.
On a different remote rack in another cabinet I have this same card being used to measure RTD's and I'm also getting no reading from those either. When I check with my meter I have mv's from the RTD but can't read it when i get online with the plc. these are 3 wire rtd's. I've included pictures of the schematics for each set of these and how they say to have the board jumper set. Any ideas??????
I think there's a typo in your part no, it should be ...KF.. not ....FK...
How is the card configured in the h/w config? - the default setting is volts, not current.
Yes my apologies on the part number. In the schematics for the system they have it one way on one page and one way on another. I will double check the hardware configuration when I get back to the plant in about an hour. For the RDT's I want the card set to A and for the 4 to 20mA coming from my drives wouldn't I use D for 2 wire current?
Why when i connect all the 8ch of Analog Input(4-20mA) into the 6ES7 331-1KF02-0AB0 module the 4-20mA reading is not correct. example the input...
2,957
Hello: Just posted a similar inquiry with regards to Rockwell HART master. Trying to figure out whether the Siemens offering is better. I need to...
4,833
Hi, I am currently using a Siemens Simatic S7 313 PLC with built in high speed counters. The issue I have is that the counter appears to increase...
4,617
We are trying to trouble shoot a Siemens IM 151-1 6es7 151-1aa03-0ab0 modual by the flashine LED but I can't find the documents for a flashing SF...
17,287
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
60