Hi everyone, hope you can help me with this

I have a S7-1200 and 3 ET200M, I want to connect 2 Siwarex U(weighing module) to each ET200M and another 2 for the S7-1200, do anybody knows if that's possible?

There's a diagram in the following link

http://imgur.com/a/aNM0o


thanks in advance

:)
 
Thank you for your answer, it was really helpful

is it possible to have the connections showed in the diagram if I use
the S7-1200 and WP231?

Best regards
 
No, You can't insert WP231 in ET200M, they have to be connected directly til a S7-1200 PLC ( you can have WP231 as Stand-alone, but then you will not have access to all parameters )
If you instead of your ET200M place a S7-1200 with the weighing modules, you can have a Master PLC with I-devices, then you will have access to all paramerters in your WP231

S7-1200 - WP231.jpg
 

Similar Topics

Hi, Is there a "rule of thumb" for Siemens logging capacity? By this I mean, if you are logging: 1 x data tag Floating point format Once per...
Replies
1
Views
1,844
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
67
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
9
Views
160
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
4
Views
141
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
Replies
1
Views
102
Back
Top Bottom