Siemens S7300, PT100 input -> 4-20mA output
Egil-s
Jul 2008
Norway
18
Hi.
I use a PT100 ipnut on a SM331 analog input module. To control the temperature in a hydraulic transmission circuit.
All I do to get right temperature displayed is this;
L PIW 290
ITD
DTR
L 1.000000e+002
/R
And my problem is:
I want to log this temperature in LabView, and the input module there is 4-20mA.
How can i send out the temperature signal from the PLC as 4-20mA?
I have tried to just move the signal from PIW 290 (PT100 input) to PQW 304 (output to LabView). The scaling isn't right.
Well, i tried that now, and i didn't get it to work.
Could you be so kind and explain more?
Wich input do i use? I cant use PIW290 straight away.
How did you arrive at this code ?
What unit is temperature in after the /R
Code:
  L   PIW  290
      ITD
      DTR
      L     1.000000e+002
      /R