Siemens - Selecting TCP/IP as the PG/PC interface on my laptop

Join Date
Jul 2002
Location
Raleigh, North Carolina
Posts
124
I cannot find the option to select TCP/IP as the PG/PC interface to connect to PLC's over ethernet. Do I have to have Simatic NET or any other packages?

Windows XP
I have Step 7 Version 5.1 SP4
ProTool 5.0
CP5511, but that is for MPI/Profibus/PPP....etc


Thanks
 
I havent done the Ethernet with Siemens yet but its my understanding you need an communication processor on both ends...ie where you now use the CP5511 you would need either a CP1613, 1411 or 1511.

Look at the literature on Siemens site and let me know if this is incorrect.
http://www.sea.siemens.com/automat/product/net/ie/auielit.html

I am sure you will need another version of Simatic NET of similar to get the drivers needed for Ethernet.
 
I got the Net 98 version to install on XP. The softnet and COM S7 software were the programs needed. The software uses your existing ethernet card as an Ethernet CP. The cp 1511 is not needed. Oh and yes, your PLC rack has to have an Ethernet CP.
 

Similar Topics

I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
64
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
9
Views
156
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
4
Views
137
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
Replies
1
Views
98
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
4
Views
135
Back
Top Bottom