Thanks Ken. I double checked my wiring and checked the output with the PLC in run and the output indicated as on yet only seeing miliVolts AC measurement.
Looks like Ive got a few things to learn before I can turn on some lights..hahaha.
I've double checked the 120V HOT neutral and ground to be connected correctly as well.
could it be that I'm missing a parameter to set for DC output on the Relay contacts?
Sorry for all the NuB questions
I can't help but think that the "Relay Output" portion is what is giving you trouble.
If you look at your outputs you will see "DC/VAC 0" and also "OUT 0" these are both contacts on that particular relay.
So if you put 24vdc from your power supply onto terminal "DC/VAC 0" and you connect your "OUTPUT" to your lamp to "OUT 0" when your program calls for O:0/0 to become true, then relay 0 will close and conduct 24vdc across its contacts and send 24vdc to your lamp.
Of course you will need to have your 24v common (or -) connected at your lamp also for it to light.
The PLC is not making 24vdc at your contact, you have to supply it.
Same goes with all the other "RELAY OUTPUTS" they are grouped together and some "Groups" have only one output contact (group 0, 1 2, & 3), some have 2 output contacts (group 4 & 5), and the the last group on your plc has 4 output contacts (group 6) that share a common voltage power terminal. (in the case of "group 6" it is DC/VAC 6 on your plc and what ever voltage you put on DC/VAC 6 will be output onto OUT8, OUT9, OUT10 & OUT11 when their corespoding output instructions become true in your program.
These are "grouped this way so you are able to output different voltages if you wish using different groups.
I think this is what you are getting stumped on, the drawing in post 4 does show you that you need to supply power to the relay contact also. Take a look at that drawing again and be sure to realize that an outside 24vdc sourse is being supplied to terminal DC/VAC0.
(YOU SAID YOUR STACK LIGHT IS 24V, SO DO NOT PUT 120VAC ON THE RELAY TERMINAL, THE DRAWING SHOWS EITHER DEPENDING ON YOUR LIGHT SO DONT LET THAT TRICK YOU INTO USING 120VAC, USE ONLY 24VDC ON THE RELAY TERMINALS FOR THIS)
If this is not where you are getting hung up and you do have the relay wiring correct then post back and we will try to help you further.
(Below is a picture with arrows to help you see how the Relay Outputs are grouped, i did not put arrows on group 6 but you will get the idea of how they work if you have not already)
Be very careful that you are not mixing 120vac where you should have 24vdc or you may never get your light module to work again.
(If for some reason you do have all the wiring correct but still do not have votage on your output then I would suspect you do not have a JSR calling your the LAD you wrote your logic in. Did you write your logic in LAD 2 or did you add another LAD? Can you hear the relay click when called in the logic? Do you have continutiy between DC/VAC0 and OUT0 when that relay is energized?)
(Hard to tell where you are getting stumped without seeing what you have or getting more feedback from you.)