Stratix 5700 CIP Studio 5000

You will need a MSG instruction. GSV/SSV instructions are only for getting data from or to the CPU. Use the MSG for any other device. Something like this.

CIP Generic
Class 35
Instance 1
Attribute 1
Specify a DINT destination Tag
 

Attachments

  • MSG Instruction.png
    MSG Instruction.png
    13.2 KB · Views: 24
Yes, this is the temperature in Celsius. The information comes from the EDS file.

21 = Class Code. The next two (20 means one value, 21 means two) values are the class. 5F and 03 is the class. Those must be swapped, so 5F 03 becomes 035F
24 = Instance. The next value is 01. That becomes the Instance
30 = Attribute. The next value is 01. That becomes the Attribute

OG
 

Attachments

  • Stratix Temperature.png
    Stratix Temperature.png
    26.7 KB · Views: 16
Following from JaxGTO, if you search in Rockwell's site for Network library, there is a library with a Stratix instruction as well as the DLR monitoring instruction.

If you're using FTView, there are faceplates, otherwise you may need to reverse engineer some of the parameters internally or the faceplate to get at that data.
 
I got it, guys! Thanks for share this knowledge. I solved my problem, using MSG instruction to get data through the parameters from EDS file. I saw the library with a Stratix instructions to create a faceplate using FTView too.
 

Similar Topics

I am in process of implementing a new network to separate the manufacturing floor from the Enterprise network. See attached basic diagram. I have...
Replies
0
Views
935
Kindly, if we enable the routing on the Rockwell Stratix 5700 switch, as in the below link, will it cause any trouble? Like for axis motion...
Replies
3
Views
145
Hi Guys, I have a Stratix 5700 managed switch that will connected to another different network thus: Stratix 1 on 10.50.3.xx >connect through...
Replies
0
Views
117
Hi All, I've been playing with 2 stratix switches in my test bench and seeing how different configurations affect the behaviour when 2 managed...
Replies
3
Views
230
Hello, I added Stratix 5700 switch (rev13.001) to Studio5000 (rev 33.02.00) as Ethernet Module but it shows mismatch/yellow triangle on the module...
Replies
6
Views
274
Back
Top Bottom