VFD won’t follow speed reference input from PLC

Kcorbelli

Member
Join Date
Feb 2023
Location
Louisiana
Posts
5
Working on 2 VFDs for two motors, they follow any speed command when local and in hand. Once I try to give a Speed reference from my PLC they both only go to the minimum frequencies. No matter what speed command I input. What could be causing this? VFD is PowerFlex 525 Allen Bradley
 
P046- 2 trm blk
P047- 3 serial/DSI (HMI)
P049- 6 4-20input

Have drawings with all VFD settings and checked in VFD itself and it matches
 
Are you using t062-t068 to use a digital input to select a speed reference? If not, the default (speed ref 1) will be used. In your case, that's the Serial/DSI. Is that how you're doing it? What PLC are you using?
 
1. Check if the VFD setting is <1 “Speed Ref 2"> on whichever of T062 - T068 selected as PLC reference.
2. Check that terminal block signal and 4-20mA current when running.
3. Check PLC program or analog module settings if no current on wire or not match expected.
4. Check wiring.
 

Similar Topics

HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
695
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
36
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
169
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
152
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
300
Back
Top Bottom