Hello, I am new in the field of PLC. Currently,i am using WAGO PLC 750-352 and I want to send digital data from my plc to server which is installed in my company. Can someone tell me what steps should I have taken to do this task?
The 750-352 is an Ethernet Coupler. You can communicate with it using several different protocols but the best one for you would be ModbusTCP. You will need a ModbusTCP driver on your server. Several OPC servers are out there such as KEPWare and Matrikon. Data from the coupler is retrieved as follows:
000001-> Digital Outputs
100001-> Digital Inputs
400001-> Analog Ouputs
300001-> Analog Inputs
For example the 5th point on the 1st Digital input module will be addressed as 100005.