SaskDreamTeam
Member
Hello Everyone,
I was wondering if any other users at plctalk.net could comment on experience configuring the I/O scanner within Unity Pro XL as well as MSTR block modbus polling on the same NOE card (slot position).
I am using a 658 Quantum controller. The CPU's ethernet port is reserved for inter-PLC communication. When the PLC was installed, all of the modbus polling to various plant equipment was configured in the I/O scanner. The I/O Scanner is configured to use Slot 4 which has an NOE Card installed. As you may know, modifications to the I/O Scanner require a write to the PLC which is extremely hard to orchestrate as they require a station outage.
I have configured 4 MSTR Blocks to manage communication between 2 new flowmeters recently installed at site. The meters are wired on a 485 string through a Schneider ETG ethernet gateway. When initiated they do not function and the MSTR block provides an error code that cannot be found in the help file.
Luckily, I had another NOE card configured in Slot 15 that is only used for the site HMI to talk to the controller on. I changed the routing address within the MSTR config and it works like a charm.
Does anyone know if NOE cards cannot handle I/O Scanning and MSTR blocks at the same time? Technical support cannot provide any case studies, wondering if anyone has had a similar experience.
Note: My I/O Scan list has 22 entries (Devices) and I am wondering if it could be a traffic problem?
Thanks for reading!
I was wondering if any other users at plctalk.net could comment on experience configuring the I/O scanner within Unity Pro XL as well as MSTR block modbus polling on the same NOE card (slot position).
I am using a 658 Quantum controller. The CPU's ethernet port is reserved for inter-PLC communication. When the PLC was installed, all of the modbus polling to various plant equipment was configured in the I/O scanner. The I/O Scanner is configured to use Slot 4 which has an NOE Card installed. As you may know, modifications to the I/O Scanner require a write to the PLC which is extremely hard to orchestrate as they require a station outage.
I have configured 4 MSTR Blocks to manage communication between 2 new flowmeters recently installed at site. The meters are wired on a 485 string through a Schneider ETG ethernet gateway. When initiated they do not function and the MSTR block provides an error code that cannot be found in the help file.
Luckily, I had another NOE card configured in Slot 15 that is only used for the site HMI to talk to the controller on. I changed the routing address within the MSTR config and it works like a charm.
Does anyone know if NOE cards cannot handle I/O Scanning and MSTR blocks at the same time? Technical support cannot provide any case studies, wondering if anyone has had a similar experience.
Note: My I/O Scan list has 22 entries (Devices) and I am wondering if it could be a traffic problem?
Thanks for reading!