We have L61 redundant existing plc. when we add new en2t module after configuring it inside the logic, the secondary going DISQ. Please advise.
The plc is offering en2t version up to 5 only. but im having en2t of v10.0 with disable keying.

Thanks.
 
Last edited:
Did you add the same module to both Chassis? Both chassis must be identical. Also the firmware of the EN2T has be be a specific version. There is a document that has the compatible versions for each module on the AB site.
 
Seyed,

For compatible versions with your L61 v.20.55 processor give this a try:
(How ever many are applicable for your application)

1756-L61: 20.055
1756-CN: 20.020
1756-CN2R: 20.020
1756-EN2T: 5.008
1756-EN2TR: 5.028
1756-RM: 3.003
1756-RM2: 20.004

I hope this helps.

Regards,
Nathan
 
The Release Notes for ControlLogix Redundancy describe the use of the new Series D hardware for the 1756-EN2T modules and have the step-by-step instructions for upgrading such a system to use the new Ethernet modules.

You absolutely must know and understand the specific Redundancy release you are using and follow those instructions precisely.

The RA Knowledgebase also discusses the topic of the new Series D Ethernet modules in Article 578295 (Access Level: Everyone).

The big firmware history list for ControlLogix Redundancy is also in the Knowlegebase, as Article 165251 (Access Level: TechConnect).
 
Thanks Mr Ken for your valuable note.

Problem solved now. as i did not connect the two cable from En2t to the same ethernet switch before.

Thanks All.
 

Similar Topics

hi, this is my first post in this forum, i have two allen bradley 1769-L30ER and unfortunately I want to make it redundancy. but I heard that...
Replies
12
Views
3,028
Hi! I am working with control logix 5570.I am facing network glitch in FT SE when controller switch from primary to sync. Chassis - I SLOT...
Replies
5
Views
2,377
Hello and thank you for taking the time to view my post! First of all, I've attached an image as reference. What I am trying to accomplish is...
Replies
4
Views
4,330
Is is possible to give some command and swap the control of primary and secondary irrespective of any fault. like using a digital input command.
Replies
1
Views
1,641
HELLO every one, i have been on CLX L73 redundant processor with following RM bundle SLOT 0 - PLC -1,2 REV 20.054 SLOT1- EN2T -1,2 REV 5.008 SLOT2...
Replies
2
Views
2,394
Back
Top Bottom