Control Logix L73 Redundancy is not stable
Dec 2015
hyderabad
HELLO every one,
i have been on CLX L73 redundant processor with following RM bundle
SLOT 0 - PLC -1,2 REV 20.054
SLOT1- EN2T -1,2 REV 5.008
SLOT2 - RM2/A-1,2 REV 20.4.6
SLOT 3- EN2TR-1,2 REV 5.008
the problem is redundancy of the system is not stable , often Secondary is refreshing & this effecting data logging in my redundant Historian system and finally effecting my vantage point reports and trends also.
kindly help me in this concern
Welcome to the Forum !
Is this a new system you are installing and commissioning, or a system that has been running for some time ? Are the problems new, or have they persisted since commissioning ?
The best tool for diagnosing Redundancy system events and problems is the "Redundancy Module Configuration Tool", or RMCT.
It is bundled along with your Redundancy release firmware so that it matches the 1756-RM modules.
You need to investigate the system using that tool to determine what is causing your Secondary switchovers.
Mr. Roach thanks for your quick response , this problem persists since the time of commissioning. some days it is stable , but completely it is not.
257
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
381
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
762
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
426
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
673