hi all,
i have a plc i need to get info from for a site im working on:
I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im trying to read from to send bools and ints to my Control Logix PLC using the MSG Instruction which in the control logix I Select 'SLC Typed Read' to read from the Micro logix.
but Im having issues with the Communication Path as it doesn't seem to work
when i enter '2, PLC IP Address' it doesn't work but im able to see this PLC in rs link and go online to it but not able to able to make online edits though.
for reference i have another plc on the same network thats a micrologix 1100 and i can read from that fine using the same method outlined above.
any help on this would be gretly appreciated.