Seyed Mohamed Member S Join Date Apr 2015 Location Al khobar Posts 39 Jan 27, 2016 #1 Is is possible to give some command and swap the control of primary and secondary irrespective of any fault. like using a digital input command.
Is is possible to give some command and swap the control of primary and secondary irrespective of any fault. like using a digital input command.
nhatsen Member N Join Date Oct 2010 Location Argentina Posts 686 Jan 28, 2016 #2 Yes, it's possible. You need to: Check Enable User Program Control on the Redundancy Module properties. Use a MSG to send a switchover to the primary Redundancy Module. You will find all you need to configure the MSG instruction in this manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um535_-en-p.pdf
Yes, it's possible. You need to: Check Enable User Program Control on the Redundancy Module properties. Use a MSG to send a switchover to the primary Redundancy Module. You will find all you need to configure the MSG instruction in this manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um535_-en-p.pdf