PV comm cable

RickParrot

Member
Join Date
Nov 2015
Location
Iowa
Posts
68
I have a PV600 (2711-T6C16L1) Ser B, Rev C, FRN 4.43 .

I successfully downloaded a PV program to it using a 2711-NC13 cable. However, that same cable isn't talking to my SLC 505. Do I need a DIFFERENT cable for that???

Thank you for your advise!o_O
 
How is the SLC5/05's serial port configured?

It has to be configured for DF1 protocol.

Which port on the PV are you using to connect to your SLC?
 
Last edited:
The PV has a RS 232, and a RS 232 DF1. I am using the RS 232 DF1. As a side note, the 505's ethernet is online and working fine. I am connecting the PV to the 505 through the RS 232 DF1 channel on the 505.
The manual you linked me confirms the 2711-NC13 cable. I thought DF1 was default on the 505's channel 0. But I will look at the 505's channel 0's settings anyway.
 
I am using the NC13 cable, and RS Linx sees the PV, but when I go to download, it says, "Error 1022 Target is not an Operator Terminal". For the Download I am using the PB32 File Transfer Type DF1 Point to Point--RSLinx AB_DF1-1.

Cant do the download. Anyone help?
 
I tried that, still got the Error 1022- Not an operator terminal. When I high-light it, it shows the PV as a 'workstation'. Should that be the case?
 
Some error messages keep saying to make sure the "printer port is disabled". What is the easiest way to get into the Configuration Screen" being that is both offline and I can't talk to it?
 
I got into the Config screen. The printer port is DISABLED. However, it says the PV is Node 2! That could be the Comm problem?!?!?
 

Similar Topics

After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
135
I was trying to connect a HMI (EZTouch Panel) to SLC500. The HMI had a PLC port (RS232/RS/422/485) 15 pin D-female connector. The PLC had a RJ45...
Replies
6
Views
2,732
I am trying to connect to a G.E. sy/max plc, the software runs on dos and it is version 2.03. I have a picture of the cable it has NRD on one end...
Replies
6
Views
1,540
Hi All, Anyone know what is the cable used to upload the backup HMI program for Stahl Exicom?
Replies
0
Views
1,498
Which communication cable should I buy to communicate with a micrologix 1200 plc. I have Windows xp sp 2 running on a virtual machine on my laptop...
Replies
2
Views
1,685
Back
Top Bottom