Dears

I have panelview 1250 with logic modules revision 8, and the runtime application is done under Rsview32, and the revision is 4,1.

When i tried to run the runtime on the panelview, it is not functioning,

So what is your advice?

Is it to doowngrade the panel view to version 4, (HoW?).
Or to upgrade the runtime to factorytalk version machine edition version 7 at least?

Thanks in advanced
 
Welcome to the Forum !

RSView32 software is different; it is an older, PC-based HMI software.

You created that application in FactoryTalk View Studio Machine Edition (ME).

The PanelView Plus terminal, if it was built for Version 8, will not support the older 4.10 firmware.

Most PanelView Plus terminals will run any older runtime file.

Do you have any details about what is not functioning about the application ? Any sorts of error messages or other information would be helpful.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
82
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
55
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
171
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
82
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
106
Back
Top Bottom