I am connecting a 4-20ma analog output from a power flex 70 ac drive to a 1769-IF4 card today.

I am using Belden 8761 for the connection which has a paper foil shield and a drain wire so should it be connected on both ends in the application or only at the source component which would be the drive in this case?

The paper foil is not connectable because it is so thin.
 
The foil shield is not meant to be connected - it's in intimate contact with the drain wire and it's the drain wire that's meant for connecting.

I generally connect the shield at the signal source.
But, have had cases where I needed to follow the advice:
Connect it only at the source - OR -
If that's not so good, connect it only at the destination - OR -
If that's not so good, connect it at both ends - OR -
failing those 3 options, do not connect it at all.
One of those four should work.
 
The foil shield is not meant to be connected - it's in intimate contact with the drain wire and it's the drain wire that's meant for connecting.

I generally connect the shield at the signal source.
But, have had cases where I needed to follow the advice:
Connect it only at the source - OR -
If that's not so good, connect it only at the destination - OR -
If that's not so good, connect it at both ends - OR -
failing those 3 options, do not connect it at all.
One of those four should work.

This is expert advice, and shows obvious experience!

The "standard" is to connect the shields at one end only. I usually did it at my panel, since I usually had more confidence in the grounding there. However, I have had installations where each of the permutations Dan mentioned worked best.:ROFLMAO:
 
The foil shield is not meant to be connected - it's in intimate contact with the drain wire and it's the drain wire that's meant for connecting.

I generally connect the shield at the signal source.
But, have had cases where I needed to follow the advice:
Connect it only at the source - OR -
If that's not so good, connect it only at the destination - OR -
If that's not so good, connect it at both ends - OR -
failing those 3 options, do not connect it at all.
One of those four should work.
This is expert advice, and shows obvious experience!

The "standard" is to connect the shields at one end only. I usually did it at my panel, since I usually had more confidence in the grounding there. However, I have had installations where each of the permutations Dan mentioned worked best.:ROFLMAO:

Tom, I appreciate your response. When I make statements like Dan's, people look at me funny - like dogs do with their heads ****ed sideways!
head-tilt1.jpg
 

Similar Topics

We have constructed a new vibrator control station with local pots on the panel and remote pots on a wireless system. We are running 6 AB 525...
Replies
5
Views
704
I will be adding contact relays and current switches to a control panel that is majority 120VAC and some 480 3-phase. The coil voltage is 24 VDC...
Replies
4
Views
2,616
Hi all, I need to send a 4-20mA signal from a PLC (ICLinks Everest) to a paperless chart recorder (Endress and Hauser RSG30) and I'm having a...
Replies
7
Views
2,259
Hello people Has anyone managed to perform an arduino communication with an omron PLC through the FINS TCP/IP protocol? I already managed to do...
Replies
3
Views
2,158
Greetings! Anyone in here have some tips for «weather proofing» a screen? I have seen solutions where a screen is built in a stainless steel...
Replies
6
Views
2,712
Back
Top Bottom