Hi Friends,

Can any one help me to figure out the maximum length for a control cable. I have devices located around 150 meters away from the controller. Is it OK to have a such a long distance ?

Can you guys tell me what precautions I need to take in order to avoid signal loss.
 
Check the manual for the PLC you are using. For an S7-1200 the distances for a 24V digital input are: 500metres shielded, 300metres unshielded and 50metres for a high speed counter input. But as I say, check the manual, if you go outside the specs of your PLC then you will have to figure out a solution.
 
Hi Friends,

Can any one help me to figure out the maximum length for a control cable. I have devices located around 150 meters away from the controller. Is it OK to have a such a long distance ?

Can you guys tell me what precautions I need to take in order to avoid signal loss.

Any specific cable?
What protocol?
 

Similar Topics

Hello all, I see that the Block Transfer Read instruction can read a max length of 64 words I have a Hilscher gateway to map DeviceNet Slave to...
Replies
7
Views
842
Anyone know off the top what the maximum cable length should be between a compact logix controller and some point I/O? I have 10 meters in my...
Replies
2
Views
1,576
Hi guys! Have been reading Profibus PA network installation guide and cannot understand the following: IEC organisation published in IEC 61158-2...
Replies
3
Views
3,086
Replies
1
Views
2,756
Hi all, I am writing a program where the user will input a bunch of individual registers they want to read. I am going to sort these registers...
Replies
2
Views
13,705
Back
Top Bottom