Hello all,
I see that the Block Transfer Read instruction can read a max length of 64 words
I have a Hilscher gateway to map DeviceNet Slave to ModbusTCP
Each input takes up 1 register/word
I have 60 devices that needs 4 words each. So that is 240 words.
Is there a way to read all the data beyond 64 words from a devicenet node?
Is there a PLC-5 involved in this ? I'm not sure where Block Transfers are coming from.
In general, a DeviceNet frame can transport 8 bytes of data, and the "fragmentation protocol" and can use multiple frames to transport larger amounts of data. There's no protocol limit but there are certainly device and practical limits to how large an I/O connection can be.
This system sounds familiar; I think I advised against using DeviceNet at all, but there were reasons.
Yes Hello Ken,
It is a PLC5 as the PLC. It just has to live like this awhile longer before our more modern PLCs gets in.
The thing is, I am using one Hilscher gateway to pull together many modbus TCP devices and then translating it to DeviceNet for the PLC5.
I am running into 200 ish words of data per Hilscher gateway, because the Emerson RSTI-OM module somehow can't splice 4 inputs worth of data onto one register (even though the manual say it can, most likely its my fault somewhere).
The maximum input mapping the 1771-DeviceNet Scanner can do is 64 words per channel...I got 2 cards, so 4 channels, but I wish I can just do 1 channel 1 card and get rid of 3 DeviceNet runs. But it seems I may have to use both channels on both cards and 4 Hilscher gateway.....
The attached screen shot shows that it takes 9 WORDS just to collect 4 inputs and 3 outputs from one RSTI-OM..although I think I can cut 2 WORDS out as those two words does nothing
So I read in the 1771-SDN manual
"The scanner module can update a maximum of 357 input words by internally linking together six different sized block transfers. "
Does that mean I can do 3-4 BTR instruction to get all of my required data into the PLC5?
I think I have my own answer. I can just select enough block transfers to accommodate my input data need. Then create BTRs with the respective block transfer size (length) to target those blocks.
Hello, I have a quick question hoping to get some clarity. I am working with a RSlogix 5 program where a PLC5 processor is communicating via...
2,624
The good news is I became a dad today, i'm posting from the hospital at this moment. the bad news is i've still not figured out reading my...
19
5,121
I am using Rslogix 500 for programing my PLC. I have analog input module. And i am using SCP instruction for scale my analog input. But in AB...
1,754
Could someone explain why and how one would is the BTW/BTR instruction in RsLogix 500? Thank you
2,403
I'm trying to do a block transfer using the cop instructions per the examples in the 1747-sn manual. There is a SLC5/03, 1747-sn ser.b, 1794-asb...
2,324