Hi guys

there is a SLC 500 controller on the floor, what I am going to do is to remove SLC500 controller and use Contrologix PLC c/w 1756-RIO module to remote control it. can anybody give me some ideas about how to handle the old SLC 500 program?

Thanks
 
I would look at putting a 1747-AENTR module in the SLC chassis so you can control it over Ethernet/IO instead of RIO.

Read this to learn how to use the translation tool to convert your SLC program to a Logix program. Note, the conversion is not 100%, you will have to run through the program correcting errors and ensuring nothing was missed.
 
First, you should consider using a 1747-AENTR adapter in the SLC-500 chassis and using ordinary ControlLogix Ethernet modules, unless you have a very good reason use the old RIO protocol network. The 1747-ASB adapter has been out of production since November 2013.

In general, SLC-500 programs can have their basic structures and data tables converted using the Logix 5000 Conversion Tool.

You should also review the hardware installed in that SLC chassis to determine if all the modules are supported by the 1747-ASB or 1747-AENTR.

The SLC/CompactLogix Migration Guide should give you an idea of the issues and tools. Even though it focuses on CompactLogix, the principles are similar.

http://literature.rockwellautomation.com/idc/groups/literature/documents/ap/1769-ap001_-en-p.pdf
 
Thanks

I will re- think about it using Ethernet, is it same thing for PLC5? what module I need to use for PLC5?

Thanks
 
100% with the 1747-AENTR card. I have done both and the AENTR is the way to go.

For the PLC 5 rack, perhaps you could take that up to a control logix rack? There are some pretty good adaptor kits available from AB that assist the wiring conversion from PLC 5 to control logix.

If I had more time I would post part numbers and details. I am pretty sure the links above will lead you there anyways.
 
Thanks

I will re- think about it using Ethernet, is it same thing for PLC5? what module I need to use for PLC5?

Thanks

PLC5 remote rack is only RIO (1771-ASB), there is no Ethernet equivalent. Any PLC5 remote racks I encounter I am converting to PointIO and currently looking at possibly using the Wago I/O system.

The conversion kit Crammed77 mentions has it's place but it's not cheap.
 
If your just looking to get the PLC5 on the network you can change the CPU to a Ethernet CPU ?

If you want to look at a program for a CLX running a SLC we did one about 10 years ago and I think I still have it, we pulled a 5/04 and put in a RIO, send me a email or PM and I can send it to you, the AENTR is another good option
 

Similar Topics

We are in the process of converting our plants from PLC5 controllers and 1771 I/O into ControlLogix PLCs and Logix I/O. Up until now we used 1756...
Replies
1
Views
86
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
Replies
1
Views
438
I have never understood how the I/O is configured using RIO. In the tree there is only the RIO module, not the racks of I/O attached or all the...
Replies
2
Views
1,311
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
Replies
15
Views
3,416
So I'm looking at replacing some obsolete Prosoft boxes that currently convert DH+ to Ethernet. I have a logix chassis that already has a...
Replies
10
Views
2,960
Back
Top Bottom