Another point I/O question

nehpets

Member
Join Date
Mar 2009
Location
Wales
Posts
496
Hi all,

This is not a problem just idle curiosity, I have recently added another point I/O station to an existing system using RSlogix5000 ver 16.03, when I tried to add a 1734-IE4C analog unit the drop down din't give me the option of a 4 channel analog unit.

My question is, is there any way of getting this option to be available for selection or is it restricted to 2 channel analog units due to the RSLogix5000 version?

Steve
 
You probably need to install an Add-on Profile (AOP) for that module if its available for that firmware revision.
 
Doh! of course, you are absolutely right - I must have had a senior moment.

Thanks for the memory jolt.

Steve
 