Hello to all.
Hope you all can give advice and help.http://www.plctalk.net/qanda/images/smilies/bow.gif
Before i start my debugging the redundancy was working fine, only 'Ring Fault" on Ring 1 and 3.
Please see architecture detail on project tree as pic. attached.
The redundancy was setup according "ControlLogix Enhanced Redundancy System, Revision 19.053_kit2".
- 1756-L61 Rev 19.52
- 1756-RM/B Rev 3.2.36
- 1756-EN2TR Rev 4.4 (all Ethernet Modules)
They are 3 DLR.
Ring 1 topology:
[Slot3 EN2TR port1 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port1].
[Slot3 EN2TR port2 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port2].
Ring 2 topology:
[Slot4 EN2TR port1 --- EN2TR IO port1].
[Slot4 EN2TR port2 --- EN2TR IO port2].
Ring 3 topology:
[Slot5 EN2TR port1 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port1].
[Slot5 EN2TR port2 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port2].
Found Slot 5 EN2TR module CIP Sync Time Synchronisation is Disable, compare with healthy ring EN2TR modules which
are Enable.See attached pictures.
Question is am i need this Time Synchronisation to be Enable?
http://www.plctalk.net/qanda/images/smilies/confused.gif
Thank you all.
Hope you all can give advice and help.http://www.plctalk.net/qanda/images/smilies/bow.gif
Before i start my debugging the redundancy was working fine, only 'Ring Fault" on Ring 1 and 3.
Please see architecture detail on project tree as pic. attached.
The redundancy was setup according "ControlLogix Enhanced Redundancy System, Revision 19.053_kit2".
- 1756-L61 Rev 19.52
- 1756-RM/B Rev 3.2.36
- 1756-EN2TR Rev 4.4 (all Ethernet Modules)
They are 3 DLR.
Ring 1 topology:
[Slot3 EN2TR port1 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port1].
[Slot3 EN2TR port2 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port2].
Ring 2 topology:
[Slot4 EN2TR port1 --- EN2TR IO port1].
[Slot4 EN2TR port2 --- EN2TR IO port2].
Ring 3 topology:
[Slot5 EN2TR port1 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port1].
[Slot5 EN2TR port2 --- CAT5/FO conv.] --- [CAT5/FO conv. --- EN2TR IO port2].
Found Slot 5 EN2TR module CIP Sync Time Synchronisation is Disable, compare with healthy ring EN2TR modules which
are Enable.See attached pictures.
Question is am i need this Time Synchronisation to be Enable?
http://www.plctalk.net/qanda/images/smilies/confused.gif
Thank you all.