Hey guys,

Have a project I am working on where I am upgrading a SLC-503 to a SLC-505. Currently the SLC-503 is conned to an old PV600(2711-K6C2) using a DH458 connection. Upgrading to a 505 is going to take away the DH485 port on the front of the controller, obviously so I am looking for options.

What I have found is a DH485/RS-232C Interface Module (1747-KE). Looking through the manual, it doesn't mention a panelView hookup, but it doesn't say you can't hook it up.

Was wondering if anyone had any experience with this?

Second option is to go to a new PV+, is there a direct swap that has Ethernet... obviously this will take much longer as I will have to convert the program installed on the PV600 to the newer model...

Thoughts are appreciated.
 
Well it looks like after some reading I found my answer... looks like i will need a 1761-NET-AIC and hoot the pannelview to CH0 (RS232) port on the 505... if i am not correct with this please let me know, otherwise, thank you!

Here's a question, Will i need to do any re-configuring on the PV itself after connecting to the NET-AIC or will it communicate properly without adjusting anything on the screen itself.
 
why not just setup the Ch 0 comms on your 5/05 from DF1 to DH485 and everything should work as you intended?

edit: after thinking about this some more, I do believe you are right in that you need the NET-AIC for it to work...
 
Last edited:
why not just setup the Ch 0 comms on your 5/05 from DF1 to DH485 and everything should work as you intended?

edit: after thinking about this some more, I do believe you are right in that you need the NET-AIC for it to work...

Why could you not CH0 to DH485? if its just one node then I think it should work, you would just need to make a cable... that said I have never done it before
 
The SLC-5/05's Channel 0 serial port is physically RS-232, but can be configured for DF1, DH485, Modbus, or ASCII protocols.

The 2711-K6C2 has only a DH485 network port (the RS485 style, with the RJ45 jack and the AMP jack).

The proper way to connect them together is to configure the SLC-5/05's Channel 0 serial port for DH485 protocol. It should be configured to use the same DH485 node address as the original SLC-5/03's Channel 1 port.

The physical connection will use a 1761-NET-AIC module. The correct cables are shown in the Net-AIC installation instructions.

And yes, if you get the SLC-5/05 serial port set for the same DH485 address as the SLC-5/03's DH485 network port, the PanelView will need no modifications.
 
Last edited:
you would just need to make a cable

I wanted to specifically mention that these devices support the same DH485 protocol, but are electrically different, so you cannot connect them directly together with copper wire. The 1761-NET-AIC provides the necessary conversion and isolation between RS-232 and RS-485 signalling.
 
thank you for all the comments and suggestions, and Ken i am glad you did mention that you can not directly connect the PLC to the PV as I would have built a cable to try and attempt this and would have failed.

Again thanks guys!!
 

Similar Topics

Hello, I was just wondering if any of you guys had a good way to run a panel view 5500 program on your desktop? I would like to create a proof of...
Replies
5
Views
2,232
Hello, I have a set of three tanks with their own trio of Hardy 6600 series load cells. Two of them have no issues with where they are at and...
Replies
3
Views
146
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
104
Hi all, Im stuck trying to support a client with Motorola ACE.. I was able to upload all of the other sites to STS but one. Im working remotely...
Replies
0
Views
113
I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
Replies
12
Views
220
Back
Top Bottom